Found this today in a house that already needs a fair bit of work. The rest of the primary loop is similarly 'well engineered'. They managed to install every single circulator in the one configuration they should not, as an air trap for the wet-rotor..... :roll:

Image


It helps explain what happened to this cast iron baseboard rad, co-incidentally located on the furthest loop of the system (2nd floor against the outside corner of the house subjected to the prevailing winds):

Image

A backside view for those of you who've not seen cast iron baseboard radiators before (I quite admire them):

Image


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 1:44 am 
Offline
Senior PHA/CER

Joined: Mon Jan 13, 2014 5:08 am
Posts: 757 [ View ]
Location: Carlsbad, Ca
Has thanked: 2783 times
Been thanked: 436 times
Not really sure what I'm looking at here, but the pump is in the wrong orientation, and what's with all the reducers? Is that a PRV?

_________________
I know of a six unit (one bedroom/bath) apartment building taht does just fine on a 3/4 water service at 60psi. No drop of pressure anywhere even with fixtures going full on. -Plumber


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 2:28 am 
Offline
Junior PHA/CER

Joined: Tue Mar 11, 2014 4:47 pm
Posts: 21 [ View ]
Has thanked: 20 times
Been thanked: 17 times
You're correct about the pump orientation, the two boiler pumps are also oriented the same way. The valve you're asking about is a Honeywell D146M1040 differential pressure regulator, but its not installed correctly either.


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 7:38 am 
Offline
Site Admin
User avatar

Joined: Sun Mar 10, 2013 6:19 pm
Posts: 9240 [ View ]
Location: Ontario
Has thanked: 3413 times
Been thanked: 7488 times
Ever join them together with that tool .. I don't know the name of the tool but it prys them or should I say squeezes them together ..

_________________
www.phac-me.com


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 8:31 am 
Offline
Shop Owner
User avatar

Joined: Fri Dec 20, 2013 10:16 pm
Posts: 1989 [ View ]
Has thanked: 809 times
Been thanked: 1473 times
A puller? Lol


Sent from my iPhone using Tapatalk


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 11:16 am 
Offline
Junior PHA/CER

Joined: Tue Mar 11, 2014 4:47 pm
Posts: 21 [ View ]
Has thanked: 20 times
Been thanked: 17 times
O.S. wrote:
Ever join them together with that tool .. I don't know the name of the tool but it prys them or should I say squeezes them together ..


Pliers and bolts? :lol: I imagine a specific plier with long handles. The interesimg thing with this place is that I re-connected with the homeowner through word-of-mouth; I had spent a significant bit of time in the house on the last major reno in 1999/2000. Whomever replaced his boilers since has left me some repair work to perform. The primary loop needs a repipe, the circulators all need re-oriented and I get to make it prettier while I'm at it, the previous 'guys with torches and wrenches' (I hesitate to call them plumbers) couldn't square, level or orient the installation to save their lives. Some of the supply & return piping is attached to the primary loop just a few feet apart and on the same side of the circulator. The system does not have zone circulators, its got pneumatic zone valves (not a lot of residential pneumatics in these parts!). The ball valves are soldered in random positions, square to nothing, parallel is a 50/50 arrangement.


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 12:26 pm 
Offline
Shop Owner
User avatar

Joined: Mon Mar 18, 2013 8:33 pm
Posts: 918 [ View ]
Location: Ontario, Canada
Has thanked: 564 times
Been thanked: 927 times
O.S. wrote:
Ever join them together with that tool .. I don't know the name of the tool but it prys them or should I say squeezes them together ..



Yeah. And I learned to dope the friction fit sleeves. Learned the hard way.

_________________
"Aint nobody got time for that" Sweet Brown


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 12:38 pm 
Offline
Junior PHA/CER

Joined: Tue Mar 11, 2014 4:47 pm
Posts: 21 [ View ]
Has thanked: 20 times
Been thanked: 17 times
MarkToo wrote:
O.S. wrote:
Ever join them together with that tool .. I don't know the name of the tool but it prys them or should I say squeezes them together ..



Yeah. And I learned to dope the friction fit sleeves. Learned the hard way.



15 years ago I had removed and re-installed most of the rads in this house during a major reno, some were relocated for the installation of French doors where windows once were. We found a place that supplied the Warden King baseboard rads refurbished. They'd salvage them from buildings, sandblast them and provide new push-nipples, trim and accessories for joining the sections. They supplied a graphite paste for use with the tapered rings. I've contacted them for a replacement for the split 24" section, but all that is available is an 18", so we'll have to have a sheet metal spacer made up. Elsewhere in the home there was some copper fin-tube rads put in, but the system only runs a single temperature, so I'll recommend some new Weil Mclain cast iron baseboards for those locations.


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 1:28 pm 
Offline
Heating Specialist

Joined: Tue Mar 12, 2013 10:53 am
Posts: 775 [ View ]
Location: west of Chicagoland
Has thanked: 490 times
Been thanked: 337 times
Needs better pixs of the boiler.. its ain't piped correctly for sure


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 1:48 pm 
Offline
Junior PHA/CER

Joined: Tue Mar 11, 2014 4:47 pm
Posts: 21 [ View ]
Has thanked: 20 times
Been thanked: 17 times
rjbphd wrote:
Needs better pixs of the boiler.. its ain't piped correctly for sure


The set-up is difficult to photograph in its entirety, I'll post a somewhat legible schematic once I've finished with my Crayolas. It consists of two Viessmann 200,000 BTU boilers and some messed-up supply and return piping. Its serving a local character home where the owner has so many other houses that he doesn't notice a lot wrong with this one.

"It's chilly, instead of calling the plumber I'll hit my Florida property bordering the exclusive golf course"


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 2:21 pm 
Offline
Heating Specialist

Joined: Tue Mar 12, 2013 10:53 am
Posts: 775 [ View ]
Location: west of Chicagoland
Has thanked: 490 times
Been thanked: 337 times
CaberTosser wrote:
rjbphd wrote:
Needs better pixs of the boiler.. its ain't piped correctly for sure


The set-up is difficult to photograph in its entirety, I'll post a somewhat legible schematic once I've finished with my Crayolas. It consists of two Viessmann 200,000 BTU boilers and some messed-up supply and return piping. Its serving a local character home where the owner has so many other houses that he doesn't notice a lot wrong with this one.

"It's chilly, instead of calling the plumber I'll hit my Florida property bordering the exclusive golf course"

Sounds like some furance company did the job..


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 8:58 pm 
Offline
Shop Owner
User avatar

Joined: Thu Mar 14, 2013 10:35 am
Posts: 1582 [ View ]
Location: Dallas, TEXAS
Has thanked: 2638 times
Been thanked: 1785 times
Image

This is safe, right?


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 10:18 pm 
Offline
Plumbing Specialist

Joined: Sat Apr 13, 2013 1:22 am
Posts: 14758 [ View ]
Has thanked: 12993 times
Been thanked: 7169 times
Hard too tell on my Iphone but isnt the expansion tank on the high side of the pump?


Top
 Profile  
 
PostPosted: Tue Apr 01, 2014 11:31 pm 
Offline
Shop Owner
User avatar

Joined: Wed Mar 13, 2013 9:59 pm
Posts: 6452 [ View ]
Location: NC
Has thanked: 2494 times
Been thanked: 3090 times
O.S. wrote:
Ever join them together with that tool .. I don't know the name of the tool but it prys them or should I say squeezes them together ..



It seems like forever and it was a BaseRay baseboard. I do not remember using any special tools. I cannot honestly remember what the heck we did with them. I am guessing we played caveman and made it work. :chicken


Top
 Profile  
 
PostPosted: Wed Apr 02, 2014 8:37 am 
Offline
Heating Specialist

Joined: Tue Mar 12, 2013 10:53 am
Posts: 775 [ View ]
Location: west of Chicagoland
Has thanked: 490 times
Been thanked: 337 times
its called radiator assy tool.. sqeeuze the sections together evenly. Have couple of them.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 17 posts ]  Go to page 1, 2  Next

   Similar Topics   Author   Replies   Views   Last post 
There are no new unread posts for this topic. What's wrong with this picture?

[ Go to page: 1, 2, 3 ]

in Service

aprilmayb

36

3310

Thu Sep 25, 2014 11:57 pm

pilot light View the latest post

There are no new unread posts for this topic. What is wrong with this Picture?

[ Go to page: 1, 2, 3 ]

in Construction

Ron

32

2882

Sun Mar 08, 2015 5:40 am

Plumbus View the latest post

There are no new unread posts for this topic. Whats the difference between Canada and USA

[ Go to page: 1, 2 ]

in Interesting Stuff

O.S.

16

1182

Fri Jun 20, 2014 10:10 pm

pilot light View the latest post

There are no new unread posts for this topic. So its been a full year, whats your favorite thread?

[ Go to page: 1, 2, 3 ]

in Interesting Stuff

ThePlumbinator

40

2843

Fri Apr 11, 2014 10:19 am

MTDUNN View the latest post

There are no new unread posts for this topic. Picture of the day

[ Go to page: 1, 2, 3 ]

in Interesting Stuff

O.S.

37

3779

Sun Nov 22, 2015 8:56 pm

johnlewismcleod View the latest post


All times are UTC - 5 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group